Is that 40lb lp tanks shown in the pic? This came up in another thread, from your layout above you have:
36” flat top 84000 btu
12” –2 burner 54000 btu
40 lb Fryer 90000 btu
Total 228000 btu +/-
Assuming you do not use more than 50% at any one time LP required would be about 114,000 btu. … Two 40’s (vapor tanks) manifold together will supply about 60,000 btu (40 deg F) to 80,000 btu (60 deg F).
Just guessing and working numbers … Looks like you need to set a manifold pressure to abt 11 or 12 wc; then set a low pressure regulator at each piece. Flat top 65% (6.5 wc); 2 burner range 50% ( 5 wc); and fryer 75% or 80% (7.5 –8 wc) … This will be about:
36” flat top 54000 btu ….. 1 burner @ 100% & 1 burner @ 50% => 27000 btu
12” –2 burner 27000 btu ….. 1 burner @ 100% => 13000 btu
40 lb Fryer 68000 btu ….. (80k –27k-13k) => 40000 btu (abt 59% on)
Total 149000 btu +/- ….. total => 80,000 btu ????
The low pressure regulators can then be adjusted to find the setting that works best with all the equipment & tanks.
I believe two 100 lb tanks would be better for your setup.
Also, I don’t see any air vents in the LP compartment. You need this for safety and the airflow is what heats the tanks to make vapor. Without the vent, the tanks will cool the compartment and slow down vapor production.
Just my 2 cents for what it's worth.